This help desk is a free resource intended for discussion purposes only. Neither BOMA, its chapters, affiliates, or Extreme Measures Inc.® are responsible for the information, comments or opinions expressed herein. For complete information, refer to the official publications of the standards themselves.

FAQ & Read-Me Articles
BOMA for Office Overview
BOMA for Industrial Overview
BOMA for Retail Overview
BOMA for Multi-Unit Residential Overview
BOMA Mixed-Use Overview
BOMA Gross Areas Overview
IPMS for Office Overview
Alternative Methodologies
Glossary of Industry Terms
What are as-built drawings / models?
What is CAD and BIM?
How do I resolve an area dispute?
Where can I get measurement standards publications?

Single-Story Building- Condo-ing

Megan
iS design
January 16, 2023

A couple questions for a single store office building:

1 )
For previous transactions a single-story building (single owner/occupant) has used the Gross Area Standard (Gross Area 1) to determine square footage (exterior face). Now, the owner of the building wants to sell a portion of the building to another party (in essence, condo-ing it) so there will now be multiple owners/occupants of the building (it is possible that some of the newly demised spaces would be leased now or in the future). Could they still use the area lines from Gross Area Standards for the square footages since there are separate owners, or would this shift over to Office Standard now since? They would not share any interior space/no common area. The setup could be likened to residential townhouses.

2a)
In Gross Area are door setback still applicable (and allowed to be included in area) in a single story building (roof overhangs above, but no second floor above). If not, could a door setback be considered external circulation?
2b)
On page 42, why is the door setback (that accesses the common area) in the upper left hand corner (near suite 100) not included on the boundary area?

3)
The building in question is about 165’ long, the front has 90’0" that is recessed approximately 4’ with roof overhanging. I would think this could be counted as “exterior circulation” typically as it is the access to the multiple doors on the front facade, however there are 32” wide columns every 7’0", that are only 24” (20” in some locations) from the building where the “circulation” would be considered. Would this be considered external circulation or are there any rules on how wide the circulation path has to be to consider is circulation? There are intersecting access sidewalks from the parking lot to each of the 3 existing doors on the front of the building.

4) There are no instances in the Gross method where Dripline/roof overhangs have effects on area?

Thanks so much!

David Fingret
Extreme Measures Inc.
January 16, 2023

Hi Megan,

1) You can continue to use the Gross Areas standard; however that areas would be split according to the Property Limit Special Conditions so each owner would receive their own report encapsulating only the area(s) that they own.

2a) Yes Exterior Door Setbacks are applicable and included in the Gross Area.
2b) It is not included because it does not meet the following required criteria:
"The height of the recessed area may not extend beyond the underside of the Floor immediately above and cannot be more than one story high." The example building has a Building Void above the Exterior Door Setback.
3) It's difficult to say without reviewing the plans; however, Unenclosed Occupant Circulation may only be applied if there are no internal corridors.
4) Dripline / Roof Overhangs generally have no impact on any areas under the Gross Areas Standard, except if the standard is being applied to an Industrial building, then "Sheltered Area" might be applicable.

Thanks,
David